water heater burning up elements catching on fire

Status
Not open for further replies.

sparky333

Member
I am a electrical service tech.I have been called to this house 3 times this week.over a water heater.( Rental property.) The Top element was smoked all chared up.The tennant said it happened the day before so her husband un pluged the cord.I checked, the circuit.Every thing looked fine 241 volts Receptacle looks brand new checked the cord perfect shape.Opened the bottom element cover.wasent burned but all rusty on tank wher the element screws in.And wet from leaking.I said the cause was from the leak.The tennant said this happenned 5 months ago too and the plumber replaced the water heater.Which i said I cant understand how a 5 month old water heater would rust that much.and so I left and said everythin electricall is ok.

Then the next day i called back.To check more into it.I checked the service.every thing was perfect all lugs tight . put the dryer on range on checked amps no problems.

Anyways the 3rd time the tennant said the power company came out and the neutral was flopping in the breeze.now iam really thinking BS.But were getting paid so i go.I get there cut the tab again.every thing was tight.So got on the phone with my boss he said go get a surge protector.So i did.then the the tennants husband was there and said the power compant tighted the lug in the meter can. My only thought about this whole thing is the plumber is trying his best to get out of warranty on the w/h and I think hes freinds with the tennants.Am i wrong ? please some one help.
 

mcclary's electrical

Senior Member
Location
VA
A loose and flopping neutral can never in any way burn up the element in a 240 volt WH. That would be impossible.

Second, China metal can rust in 3 days, let alone 5 months
 

sparky333

Member
thanks for the responses

thanks for the responses

I told the tennant the same thing.about a loose neutral would not burn up a water/heater 240v circuit.just 120v circuits.I just posted this because that calls been annoying.When i see nothing wrong.And I hate liars worse then anything.I know Bussiness people lie constantly.Evan my bosses They say its part of doing bussiness,they think of them as white lies.It still a lie.Sorry for venting.I just like doing the best job i can.Enjoy electrical work >and rember saftey :roll:First.
 

hurk27

Senior Member
sounds like the water was turned off and the water heater tank got inadvertently drained, this is the only way I have seen elements burned up like that, I would check if the city had the water off, or they had turned off there well if they have one, happens all the time in trailer parks when the park goes to do maintenance and doesn't give home owners notice. I have dealt with the same thing with the homeowners trying to blame my work, but with a 240 volt circuit there is no way unless the transformer primary has a few loops shorted together which will lower the turn ratio and cause a higher output, but that is so very rare and it would show up as a high L to L and L to N reading, this is a common cry on hot tubs, when the heating element burns up, and with a hot tub the biggest mistake is when a home owner goes to clean it out, and does not turn off the breaker or disconnect, then they leave it dry and power goes out and comes back on, which almost all hot tubs default to pump and heat anytime power goes out because of so many out in the cold in the winter. or they will turn the breaker back on after they start filling it, but haven't got enough in it to reach the pump inlet.

I just am very assertive with them and tell them there is nothing electrical that can cause this, the only thing is running it dry.
 

76nemo

Senior Member
Location
Ogdensburg, NY
sounds like the water was turned off and the water heater tank got inadvertently drained, this is the only way I have seen elements burned up like that, I would check if the city had the water off, or they had turned off there well if they have one, happens all the time in trailer parks when the park goes to do maintenance and doesn't give home owners notice. I have dealt with the same thing with the homeowners trying to blame my work, but with a 240 volt circuit there is no way unless the transformer primary has a few loops shorted together which will lower the turn ratio and cause a higher output, but that is so very rare and it would show up as a high L to L and L to N reading, this is a common cry on hot tubs, when the heating element burns up, and with a hot tub the biggest mistake is when a home owner goes to clean it out, and does not turn off the breaker or disconnect, then they leave it dry and power goes out and comes back on, which almost all hot tubs default to pump and heat anytime power goes out because of so many out in the cold in the winter. or they will turn the breaker back on after they start filling it, but haven't got enough in it to reach the pump inlet.

I just am very assertive with them and tell them there is nothing electrical that can cause this, the only thing is running it dry.

;) Then the deer in headlight stare. :roll:
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Now I have rented un-furnished apartments before, and even had to supply my own window AC unit, but never a BYO hot water heater one LOL:grin:

Or did you mean "take it with you" hot water heater:roll:
The latter. :cool:
 