Thread: 2-hour fire rated pull box, wireway?

  1. #1
    Join Date
    Jun 2007
    Posts
    648

    Cool 2-hour fire rated pull box, wireway?

    Does anyone know who make 2-hour fire rated wire way or pull box? Tks

  2. #2
    Join Date
    Dec 2010
    Posts
    322
    If you look at UL listing for Metallic Outlet Boxes (QCIT), it seems that any listed metal box can acheive a 2-hour rating when installed in accordance with that listing.

  3. #3
    Join Date
    Jun 2006
    Location
    Westchester County NY
    Posts
    144

    2 hour rated pullbox

    Anbm,

    The problem is that as per building code you are limited to a membrane penetration of 16 square inches per opening.

    You can always try to get the two hour wall built around (and behind) the box or wireway.

    Raider is good with the building code, maybe he will chime in.

    Joe Villani

  4. #4
    Join Date
    Jun 2007
    Posts
    648
    I am looking for a wire way/or pull box to be installed in a room without with 2 hour fire rated wall.

  5. #5
    Join Date
    Nov 2008
    Location
    Chapmansboro,Tn.
    Posts
    25
    Quote Originally Posted by anbm View Post
    I am looking for a wire way/or pull box to be installed in a room without with 2 hour fire rated wall.
    Local code around here requires you to wrap the outside of the box with 2 hour fire rated puddy pads.