Page 2 of 2 FirstFirst 12
Results 11 to 16 of 16
Thread: Grounding a 320 Meter base
  1. #11
    Join Date
    Jul 2003
    Posts
    349
    How would run the gec from the meter can to where?
  2. #12
    Join Date
    Jun 2005
    Logan, Utah
    Posts
    8,200
    Quote Originally Posted by wmeek View Post
    The the grounding electrode.
    The GEC is used to connect the grounded service conductor to the grounding electrode system. The connection to the grounded conductor can be at the meter base.
    Chris
  3. #13
    Join Date
    Jul 2003
    Posts
    349
    So if I run a GEC to the neutral in the service disconnect and install main bonding jumper there, that you do not have to run a seperate GEC to meter can
  4. #14
    Join Date
    Feb 2003
    Fl
    Posts
    17,094
    So you are saying that if you bond the neutral in the service disconnect(Main bonding Jumper) , you do not have to run another GEC to the meter can.
    If the GEC is landed in the meter can that is the only GEC needed.
    Roger
    Join Date
    Jun 2005
    Logan, Utah
    Posts
    8,200
    Is the meter can a remote meter can from the rest of the service?
    Chris
  6. #16
    Join Date
    Jan 2008
    Raeford, NC
    Posts
    3,682
    If the poco is requiring it to be bonded in the meter base bring the #6 to the neutral bar in the meter can with the neutral ( grounded conductor). From there you run the hots (ungrounded conductors) and the neutral to the FIRST disconnecting means neutral bar. This bar must be bonded to the can ether by the bonding screw or bar