Thread: You make the call: NEC 110.26

  1. #1
    Join Date
    Mar 2008
    Location
    In a house
    Posts
    1,100

    You make the call: NEC 110.26

    Do you think that this installation (all new) with the natural gas line run below the main panel to be a violation of 110.26(F)(1)(a) OR would you say it is acceptable under 110.26(F)(1)(b) ?

    Sorry for the fuzzy picture

    "If you always do what is right to others you can't go wrong"

    The more I learn, the more I realize just how much I don't know.

    Always consult your local code enforcement department for direction. Read at your own risk

  2. #2
    Join Date
    Feb 2003
    Location
    NE Arkansas
    Posts
    2,222
    "Workspace" is measured from the FACE of the panel. Therefor, the entire wall face is outside the working space. There is no violation, since that is a surface mounted panel.

    Had the panel been flush mounted there would be a violation.

  3. #3
    Join Date
    Feb 2003
    Location
    Ohio
    Posts
    989
    I say violation of 110.26(F)(1)(a). 110.26(F)(1)(b) simply states that foriegn systems are allowed ABOVE the dedicated space if adequate protection is provided for the electrical equipment below (i.e. leak protection).

    Pete
    Experience is something thats gained shortly after you really needed it.

  4. #4
    Join Date
    Jul 2008
    Location
    nyc
    Posts
    217
    Violation,above and below panel are dedicated electrical space 110.26(f)(1).
    cmac1

  5. #5
    Join Date
    Mar 2008
    Location
    In a house
    Posts
    1,100
    Quote Originally Posted by renosteinke View Post
    "Workspace" is measured from the FACE of the panel. Therefor, the entire wall face is outside the working space. There is no violation, since that is a surface mounted panel.

    Had the panel been flush mounted there would be a violation.
    Can you specify a code section for that please?
    "If you always do what is right to others you can't go wrong"

    The more I learn, the more I realize just how much I don't know.

    Always consult your local code enforcement department for direction. Read at your own risk

  6. #6
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    49,012
    Quote Originally Posted by ivsenroute View Post
    Do you think that this installation (all new) with the natural gas line run below the main panel to be a violation of 110.26(F)(1)(a) OR would you say it is acceptable under 110.26(F)(1)(b) ?

    Yes I do think it is a violation.

    It is the same violation that occurs each time a panel is mounted flush in a wall with a bottom plate.

  7. #7
    Join Date
    Jan 2009
    Location
    Easton, Maryland NEC: 2011
    Posts
    7,866
    Quote Originally Posted by ivsenroute View Post
    Can you specify a code section for that please?
    Maybe this?

    110.26(1) Depth of Working Space. The depth of the working
    space in the direction of live parts shall not be less than that
    specified in Table 110.26(A)(1) unless the requirements of
    110.26(A)(1)(a), (A)(1)(b), or (A)(1)(c) are met. Distances
    shall be measured from the exposed live parts or from the
    enclosure or opening if the live parts are enclosed.
    "Electricity is really just organized lightning." George Carlin


    Derék

  8. #8
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    49,012
    Quote Originally Posted by renosteinke View Post
    "Workspace" is measured from the FACE of the panel. Therefor, the entire wall face is outside the working space. There is no violation, since that is a surface mounted panel.

    Had the panel been flush mounted there would be a violation.
    The question has nothing to do with workspace, it has to do with Dedicated Equipment Space.

  9. #9
    Join Date
    Mar 2008
    Location
    In a house
    Posts
    1,100
    Quote Originally Posted by iwire View Post
    The question has nothing to do with workspace, it has to do with Dedicated Equipment Space.
    Agree
    "If you always do what is right to others you can't go wrong"

    The more I learn, the more I realize just how much I don't know.

    Always consult your local code enforcement department for direction. Read at your own risk

  10. #10
    Join Date
    Jan 2009
    Location
    Easton, Maryland NEC: 2011
    Posts
    7,866
    Quote Originally Posted by iwire View Post
    The question has nothing to do with workspace, it has to do with Dedicated Equipment Space.
    Quote Originally Posted by ivsenroute View Post
    Agree
    Aw crapola, outgunned by two damn yankees this time.
    "Electricity is really just organized lightning." George Carlin


    Derék