Is it acceptable to use LFMC on the load side of a CT Cabinet, to the line side of the first means of disconnect? The LFMC run is less than 6ft

Yes, 230.43. You would have to pay attention to the extra bonding requirements though. Some POCOs may have an issue with this even though the NEC permits it.
 