Thread: copper feeder size for 3-phase 4-wire 225 amp OCP use 3/0 or 4/0?

  1. #21
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    25,853
    Quote Originally Posted by Team-MEI View Post
    (4) #4/0 and (1) #6 XHHW–compact fits in (1) 2" EMT.
    Again why #6... Isn't this a 225 amp breaker?

  2. #22
    Join Date
    Sep 2009
    Location
    Los Angeles, Ca
    Posts
    646
    Quote Originally Posted by Dennis Alwon View Post
    Again why #6... Isn't this a 225 amp breaker?
    #6 is based on 200A OCPD size per art. 250. It is a common installation since 4/0 may be specified due to Voltage Drop. The reason why EGC wire is considered is that many engineers and indeed many internal specifications for clients, ranging from universities to defense contractors to military, call for an EGC wires (the merits of which, or lackethereof, have been discussed a considerable number of times on this forum and elsewhere). I'm pretty sure you've been involved in many of those threads so you should have a good idea of both sides of arguments for this practice

  3. #23
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    48,429
    Quote Originally Posted by tkb View Post
    Your calculation only calculated the area of the conductors and not the fill of the conduit.
    You need to divide the conductor area by the conduit area to get the percentage of fill.
    I don't have to figure the percentage, I just can't exceed what is shown in the column of Table 4.

  4. #24
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    25,853
    Quote Originally Posted by skeshesh View Post
    #6 is based on 200A OCPD size per art. 250. It is a common installation since 4/0 may be specified due to Voltage Drop. The reason why EGC wire is considered is that many engineers and indeed many internal specifications for clients, ranging from universities to defense contractors to military, call for an EGC wires (the merits of which, or lackethereof, have been discussed a considerable number of times on this forum and elsewhere). I'm pretty sure you've been involved in many of those threads so you should have a good idea of both sides of arguments for this practice
    I understand that but I thought the op was using 4/0 for a 225 amp breaker.

    per NEC 240.4B & 240.6 is it allowable to use 3/0 on a 225A ckt bkr? (for a non-continuous rated load).

  5. #25
    Join Date
    Jul 2003
    Location
    MA
    Posts
    1,579
    Quote Originally Posted by iwire View Post
    I don't have to figure the percentage, I just can't exceed what is shown in the column of Table 4.
    It does exceed Table 4.
    Table 4 for 2" EMT = 1.342
    Area of conductors = 1.3455

    You rounded your calculation down to 1.34

    Also as Dennis stated, you cannot use this a 225a feeder without a #4 ground. Needs 2-1/2" EMT
    Last edited by tkb; 02-15-11 at 09:07 PM. Reason: additional stuff
    Tim
    Master Electrician
    New England
    Yesterday's Technology at Tomorrow's Prices

    Answers based on 2011 NEC

  6. #26
    Join Date
    Feb 2003
    Location
    Portage, Indiana NEC: 2008
    Posts
    9,747
    Quote Originally Posted by skeshesh View Post
    #6 is based on 200A OCPD size per art. 250. It is a common installation since 4/0 may be specified due to Voltage Drop. The reason why EGC wire is considered is that many engineers and indeed many internal specifications for clients, ranging from universities to defense contractors to military, call for an EGC wires (the merits of which, or lackethereof, have been discussed a considerable number of times on this forum and elsewhere). I'm pretty sure you've been involved in many of those threads so you should have a good idea of both sides of arguments for this practice
    If you have up the current carrying conductors for voltage drop you would still have to up the EGC one size so even with 4/0 on a 200 amp breaker you would still have a #4 EGC. so its 3/0 on a 200 with a #6 EGC max for existing conduit, or you use the conduit for the EGC.

    But the OP states 3 phase 4-wire which I take as meaning 3 phase conductors and a neutral not an EGC?
    Last edited by hurk27; 02-16-11 at 12:44 AM.
    Wayne A. From: N.W.Indiana
    Be Fair, Be Safe
    Just don't be fairly safe

  7. #27
    Join Date
    Feb 2003
    Location
    Portage, Indiana NEC: 2008
    Posts
    9,747
    I would agree with the OPer if the load is a motor load, in which he could install 3/0 and have a 225 amp breaker, but then a neutral wouldn't be needed, so I guess more input is needed:grin:
    Wayne A. From: N.W.Indiana
    Be Fair, Be Safe
    Just don't be fairly safe

  8. #28
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    48,429
    Quote Originally Posted by tkb View Post
    It does exceed Table 4.
    Table 4 for 2" EMT = 1.342
    Area of conductors = 1.3455

    You rounded your calculation down to 1.34
    I did not round anything down, I simply calculated it to two places. How many places does the NEC require?

    I still ask ......... where does it say I cannot calculate it this way.


    Also as Dennis stated, you cannot use this a 225a feeder without a #4 ground.



    I mentioned that way back in post 11. :grin:

  9. #29
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    19,048
    My opinion is that you use the number of decimals that you have in the code book. So for the wire area you use 4 and for the conduit area you use 3.
    Don, Illinois
    "It is the first responsibility of every citizen to question authority." B Franklin

  10. #30
    Join Date
    Jul 2003
    Location
    MA
    Posts
    1,579
    Quote Originally Posted by iwire View Post
    They are sitting on my desk at work.

    From Table 4:

    2 EMT area for more than 2 'wires' 1.342 sq in.

    From Table 8:

    4/0 THHN = 0.3237 * 4 = 1.2948

    6 THHN = 0.0507

    1.2948+.0507=1.34. :grin:
    Quote Originally Posted by iwire View Post
    I did not round anything down, I simply calculated it to two places. How many places does the NEC require?

    I still ask ......... where does it say I cannot calculate it this way.







    I mentioned that way back in post 11. :grin:
    It looks like rounding down to me.

    1.2948+.0507=1.3455
    Rounded to two decimal places = 1.35, thus over 40%
    If the NEC gives you 4 decimal places that is the accuracy they are looking for.
    Tim
    Master Electrician
    New England
    Yesterday's Technology at Tomorrow's Prices

    Answers based on 2011 NEC