Annex D - Example D1(a) mistake?

Status
Not open for further replies.
In going over the example D1(a) in the 2008 NEC book, I noticed that the Bathroom Branch Circuit (1, 2-wire, 20A circuit) is not included in the load calculation.

Is this an omission or error of the authors? Or is there a section that I missed classifying this as an intermittent load that need not be accounted for in load calculations?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
This is not an error of omission. The bathroom circuit is included as part of the general lighting/receptacle loads. See 220.14(J)(1) and 210.121(C)(3).
 
Status
Not open for further replies.