Page 1 of 2 12 LastLast
Results 1 to 10 of 11
Thread: Low voltage cutoff for 12vdc gel cell battery
  1. #1
    Join Date
    Feb 2003
    Bremerton, Washington
    Posts
    7,833
    I need to design a low voltage cutoff circuit for a 12 VDC gel cell battery, that normally is on a charger at 13.7 volts
    The circuit will open a relay before the battery voltage drops too low making the recharge cycle too long.
    (common battery as used in fire and intrusion panels)
    Whats a reasonable voltage for a cutoff circuit?
    Moderator-Washington State
    Ancora Imparo
  2. #2
    Join Date
    Apr 2008
    Ann Arbor, Michigan
    Posts
    6,833
    110308-2252
    Tom:
    I can not answer your question. I suggest you contact the battery manufacturer.
    The voltage will be be temperature dependent to some extent. This may be of concern.
    The real question could be what is an optimum charging philosophy for maximum life of the battery.
    Following is some very limited information:
    A Power-Sonic PS-1270 F1 12 V 7.0 Amp. Hr. Sealed Rechargeable battery.
    It has been setting on the shelf for many months since I last recharged it.
    Room temperature is about 68 deg F. Current voltage read 12.25 V. Started a 200 MA charge and after a few minutes it was up to 12.68 V. This battery is probably at least 5 years old. Made in China.
    By contrast a battery pair I bought to replace batteries in a UPS, but never installed had very poor storage life. These were made in Taiwan.
    A Die-Hard Marine setting in the garage at about 35 deg F and not charged in about the last month is 12.82 V.
    I doubt you really want battery steady-state unloaded voltage to drop noticeably as a criteria of when to charge a battery.
    The particular battery manufacturer may be very important to your question.
  3. #3
    Join Date
    Jan 2007
    Michigan
    Posts
    699
    Evrything I hear about gel-cell's they do just fine with a constant charge.
    Don't you mean cut-out when voltage gets too HIGH? When a battery is discharged the voltage is low and when the charge completes it is High.
    Best advice is from battery manufacture. Your looking for 2.35v per cell.
    13.7V sounds a little low. 14.4V is ideal and I would let it float charge rather than cut out when charged.
    John,
  4. #4
    Join Date
    Jul 2009
    Ware Shoals, South Carolina
    Posts
    1,200
    You may be looking for something like this:
    http://www.homesecuritystore.com/p-4...er-switch.aspx
    I do not think it has a voltage adjustment. You may be able to modify this easier than building from scratch.
    Advise is a dangerous gift, even from the wise to the wise.
  5. #5
    Join Date
    Jul 2006
    San Francisco bay area
    Posts
    279
    Rats! You beat me to it!
    Quote Originally Posted by SG-1 View Post
    There is also this:
    http://products.boschsecurity.us/en/...0e4836d4a0a649
    The Bosch D135A cuts off the battery at 9.5 volts, as opposed to 10 volts for the Elk model.
    S'mise: 14.4 volts may work as a 'fast charge' rate (or as the starting charging voltage that later tapers off), but as a constant trickle charge 14.4 volts will reduce the service life of a sealed lead-acid battery. 13.65 - 13.67 volts is ideal for a constant trickle charge.
    In battle, in forest, at the precipice in the mountains,
    On the dark great sea, in the midst of javelins and arrows,
    In sleep, in confusion, in the depths of shame,
    The good deeds a man has done before defend him.
    --Bhagavad-Gita
  6. #6
    Join Date
    Feb 2003
    Posts
    7,833
    Just to clarify the low voltage cutoff is when the equipment is running on battery with no ac power.If I can cut it off before the voltage gets too low, then it will recharge faster when AC returns.
    Ancora Imparo
  7. #7
    Join Date
    Apr 2008
    Ann Arbor, Michigan
    Posts
    6,833
    110309-1444 EST
    Tom:
    Study this site and others and see if its enough information. http://www.hydrolynx.com/_manuals/5031.pdf
    I used
    gel cell voltage level vs charge level
    as the search string.
  8. #8
    Join Date
    Jun 2010
    Posts
    1,928
    The cut-off voltage should be based on parameters desired, such as maximum battery longevity or run time, as well as the load current.
    The cut-off though, maybe limited by the device's minimum operable voltage.
    For applications that draw enough current to cause more than a few percent of voltage drop, I don't like conventional cut-off voltage sensing, because it causes premature dropping before device's minimum voltage has been reached to "protect" the battery. Voltage drop is significant at lower voltage and there should be a second pair of sensing wires that go directly to the battery.
  9. #9
    Join Date
    Nov 2008
    Twin Cities, MN
    Posts
    83
    What is the application this is for? Why do you want to limit the recharge time for the battery?
  10. #10
    Join Date
    Jan 2011
    DC area
    Posts
    810
    Using either of these ICs
    http://www.national.com/mpf/LM/LM10.html#Overview
    http://www.national.com/mpf/LM/LM311.html#Overview
    is a good starting point.
    You'll need hysteresis because the battery voltage may rebound once the load is removed. You may also want an indicating LED telling you that the thing has fired. You might find a way to power the circuit from the battery being monitored.
    Once you post a circuit from the Web, changing one or two resistor values will probably make it work for your application.
    This thing is so simple it is almost guaranteed to work the first time, but just in case you get weird readings on your meter during troubleshooting it helps to have an o'scope with a relatively wide bandwidth nearby.
    You can get the parts from Hosfelt, Allelectronics or similar places.
Posting Permissions
  • You may not post replies
  • You may not edit your posts