all i did was install 1 30kva transformer feeding a panel
with 1 3pole 100 1 2pole 100
5 -1 pole 20.
yes i know thats wrong.
but he quoted 450.3 b.2
then he hits me with 250.21c.
disconnect not provided coduit in 25ft of secondary transformer feed.
now 250.21c does not say that
this is 2005 code.
l
with 1 3pole 100 1 2pole 100
5 -1 pole 20.
yes i know thats wrong.
but he quoted 450.3 b.2
then he hits me with 250.21c.
disconnect not provided coduit in 25ft of secondary transformer feed.
now 250.21c does not say that
this is 2005 code.