Results 1 to 8 of 8
Thread: electrical outlets above electric baseboard heat
  1. #1
    Join Date
    Nov 2007
    Posts
    120
    I cannot remember, but are electrical outlets permitted to be installed above electric baseboard heaters in dwellings? I have a 10' span of baseboard heater and would like to install an outlet within that span. Thanks
  2. #2
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    32,851
    Quote Originally Posted by Ken 6789 View Post
    It is a manufacturers installation that will not allow receptacles above a baseboard heater. They make an accessory for receptacles at the ends of the heater.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  3. #3
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    32,851
    Check this out
    210.52 Dwelling Unit Receptacle Outlets.
    This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. The receptacles required by this section shall be in addition to any receptacle that is:
    (1) Part of a luminaire or appliance, or
    (2) Controlled by a wall switch in accordance with 210.70(A)(1), Exception No. 1, or
    (3) Located within cabinets or cupboards, or
    (4) Located more than 1.7 m (5 ft) above the floor
    Permanently installed electric baseboard heaters equipped with factory-installed receptacle outlets or outlets provided as a separate assembly by the manufacturer shall be permitted as the required outlet or outlets for the wall space utilized by such permanently installed heaters. Such receptacle outlets shall not be connected to the heater circuits.
    FPN: Listed baseboard heaters include instructions that may not permit their installation below receptacle outlets.
  4. #4
    Join Date
    May 2008
    Palmer, MA
    Posts
    485
    It only shows up as a FPN in 210.52.
    Guess I should have refreshed before I posted.. sorry Dennis
  5. #5
    Join Date
    Jun 2005
    Delmarva, USA
    Posts
    1,645
    We got around that by installing (2) 5-foot sections of BB heat, with the receptacle outlet mounted above the non-heating portions in the center between the 2 units.
    Much cheaper than those receptacle accessories made for the units, IMO.
  6. #6
    Join Date
    Mar 2008
    Roebling, NJ
    Posts
    111
    Our inspectors always told us that receptacles had to be at least 1 foot from the end of any electric baseboard heaters if not installed in the heaters as per specs.
  7. #7
    Join Date
    Nov 2007
    Posts
    120
    Quote Originally Posted by kbsparky View Post
    This is a good idea! Thanks for all replies
  8. #8
    Join Date
    Feb 2007
    Alexandria, VA
    Posts
    390
    unit mounted receptacle
    The accessory for the receptacle is for the end of the unit. How useful are these since the need for a receptacle is mostly in the middle of the unit and not at the end where a wall receptacle may be able to be installed?
Posting Permissions
  • You may not post replies
  • You may not edit your posts