    Core Drill & Rebar

    Anytime you core drill through a slab I imagine you can hit rebar. Is x-raying of a slab always required and if not how to you avoid the rebar? THanks.

  2. #2
    Join Date
    Sep 2004
    Location
    Durham, NC
    Posts
    5,272
    Static poured floors for conversation is not a problem the holes are to small, Dynamic Floors that are loaded with pulled tension strains is a whole different story. X-ray any tension floor.
    If your even thirsty, your two quarts low.

  3. #3
    Join Date
    Jul 2008
    Location
    NJ
    Posts
    1,880
    Quote Originally Posted by cadpoint View Post
    Static poured floors for conversation is not a problem the holes are to small, Dynamic Floors that are loaded with pulled tension strains is a whole different story. X-ray any tension floor.
    Ok and I guess the structural spec has t be reviewed in order to tell what kind of slab has been poured, post/pre tention etc.???? Thanks.

  4. #4
    Join Date
    Jul 2008
    Posts
    774
    None prestressed slabs with re-bar are no match for a coring machine -- just goes a little slower as you go thru the rebar. Of course it can go thru a raceway too???

  5. #5
    Join Date
    Sep 2005
    Location
    western suburbs, chicago
    Posts
    127
    The issue is not whether the bit will cut through the prestressing member, but whether the floor will loose too much strength if the member is cut. Many prestressed floors a prefab slabs with cable tunnels. These tunnels could be located with a small drill without cutting the cable.

  6. #6
    Join Date
    Feb 2003
    Location
    Portage, Indiana NEC: 2008
    Posts
    9,890
    Just use a good metal detector/locator's, in the past I have even used those ones that retired people comb the beach with

    Cutting into a pretensioned cable is not a good thing and can be a very costly mistake!
    Wayne A. From: N.W.Indiana
    Be Fair, Be Safe
    Just don't be fairly safe

  7. #7
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    21,838
    Quote Originally Posted by hurk27 View Post
    Cutting into a pretensioned cable is not a good thing and can be a very costly mistake!
    It makes a big noise that can be heard throughout the building, too. Trust me.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  8. #8
    Join Date
    Apr 2004
    Location
    Back in Alaska, on a "Jack Bauer" job!
    Posts
    1,708
    X-ray is way smart in questionable territory. Better to lose the job to "Joe-cheapo" than be explaining to your insurance agent "Then there was this loud sound, and ,and ,and..."

    Risk analysis depends on a lot of factors. Choose wisely!
    Don't let fear be your guide!

  9. #9
    Join Date
    Apr 2011
    Location
    Northern Virginia
    Posts
    17

    Rebar detection

    I worked over 20 years at Diablo Canyon NPP, where is was forbidden to cut rebar during core drilling. We used a ground detector device that plugged into a grounded receptacle, then the core drill plugged into this device. When any metal was encountered during the drilling process the unit tripped. I have been unable to locate one of these devices, as the question just came up at my new job on how to avoid cutting the rebar. This inexpensive device alleviated the need for X-ray, GPR, or magnetic imaging. Where do I find one of these devices? What is it called?

    Thanks.

  10. #10
    Join Date
    Apr 2007
    Location
    Huntington Beach, CA (21 Hrs. 32 Min. from Winged Horses)
    Posts
    3,605
    Quote Originally Posted by horsegoer View Post
    Anytime you core drill through a slab I imagine you can hit rebar. Is x-raying of a slab always required and if not how to you avoid the rebar? THanks.
    milwualkee makes a metal detector for about $400 that works well..... i've
    verified results right alongside a guy doing ultrasound, and i'd trust it,
    but not on a POST TENSION deck.

    cables on post tension are 1/2" cable, sheathed in greased sleeves, pulled to
    20,000 lbs tension, most of the time.

    i broke one, once, in 1984, on the meridian hotel across from john wayne
    airport. i was trying to locate a buried red dot in the slab, and was directed
    by my foreman to do so with a hilti TE 72 with a bull point on it.

    i just barely nicked it, and the sound was like a 30-06 going off in a tile
    bathroom. the cable came out the side of the building, went across the
    parking lot, as it was 4 floors up, and went thru the glass on the office
    building next door. it also blows out chuncks of concrete 6" wide and
    4' long, where the peaks and valleys in the cable are at in the slab.

    nobody was hurt.

    repair of the cable back then was $15,000.
    now, it runs about $80,000 i was told recently.

    post tension, i x-ray before hand with a licensed guy... then i use
    my metal detector over the area to detect any metal before i cut,
    and i get my lucky rabbits foot out of the work truck as well, in
    case i need it.


    randy
    “Give a person a fish and you feed them for a day;
    teach that person to use the Internet and they won't bother you for weeks.”