Not necessarily. A typical "two gang" meter socket used in this application may have single line side lugs that accept up to (1) 250 or 300 KCMIL conductors. If no main breakers incuded in the enclosure, and 100/125 amp meter jaws, it may only accept up to (1) 2/0 load side conductors.Go parallel in, separate out? Right?