Page 1 of 2 12 LastLast
Results 1 to 10 of 15
Thread: Life Safety and Critical Care circuit separation
  1. #1
    Join Date
    Sep 2010
    Posts
    27
    Plan review has turned us down because we have set a panel beside of the generator to distribute the generator power at a nursing home. They say we cannot share the Life Safety and the Critical Care power after it leaves the generator. This is a new building with one Life Safety ATS and three Critical Care ATS. Their recomendation is to set a trough inside of the generator and tap these panels in the trough. I'm probably wrong but I never thought that the seperation applied before the transfer switch. Any thoughts?
  2. #2
    Join Date
    Feb 2003
    Fl
    Posts
    16,800
    See the FPN Figures 517.41 #1 and #2
    Roger
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,747
    I have had a similar situation. The plan reviewer's concern was that the generator had a circuit breaker of its own, and the separation into different groups happened after that point. We removed the generator breaker, and the plan reviewer approved the design.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  4. #4
    Join Date
    Jan 2009
    Smyrna, Georgia
    Posts
    34
    I'm not sure I understand the difference whether the overcurrent protection devices are within the generator enclosure or in a panel outside of the enclosure. It is my understanding the the division between the systems happens after the automatic transfer switches, not before. Have you reviewed NFPA 99, chapter 3 or NFPA 110 to help determine what defines the start of the branches?
    I have fed multiple ATS in the past (critical branch, life safety, equipment branch) from a panel fed by a transformer and not had an issue with inspections.
    Chris
  5. #5
    Join Date
    Feb 2003
    Fl
    Posts
    16,800
    Chris, see page 47 of this document to see what NC wants
    Roger
    Join Date
    Jan 2009
    Smyrna, Georgia
    Posts
    34
    Roger,
    That is interesting, but does it have basis in code or is the seperation just required for State of NC owned projects. I don't have my NFPA 99/110 with me right now or I would research.
    Chris
  7. #7
    Join Date
    Feb 2003
    Fl
    Posts
    16,800
    Chris, the NC illustrations are basically the same illustrations shown under 700.9(B) of the NECH.
    Roger
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,747
    Quote Originally Posted by Chris3585 View Post
    In my case, the problem was having both. The plan reviewer's take on the requirements was that the separation rules applied as soon as you cross the first overcurrent device or the first ATS. So if there is a generator breaker, and you have a single feeder going from there to a panel, and you plan to serve both emergency and non-emergency loads from the panel, then you have violated the separation requirements. The feeder from the generator breaker to the panel has both types of loads.
    So I was essentially posing the question of whether the installation under discussion includes a generator breaker upstream of the panel.
  9. #9
    Join Date
    Jun 2003
    Posts
    6,801
    Quote Originally Posted by roger View Post
    Roger
    Roger:
    Maybe the 2011 is different, but in the 2008 Handbook, illustration 700.3 specifically shows a single main breaker is OK as long as it is selectively coordinated (700.9(5)(b) exception).
    Also, since both the Critial Branch and the Life Safety Branches are part of the emergency system, aren't they both Article 700 loads? So I'm not sure the illustrations in Article 700 apply the same as they would to an emergency load and a non-emergency load.
    Steve
  10. #10
    Join Date
    Sep 2009
    Los Angeles, Ca
    Posts
    646
    Quote Originally Posted by charlie b View Post
    Was the sole purpose of above mentioned breaker protecting the conductors from the generator to the distribution? And are you saying that you there was no main breaker used in the distribution board? How was the feeder overcurrent protection accomplished?
Tags for this Thread