GFCI on AFCI Breakers

Status
Not open for further replies.

GeorgeKoehl

Member
Location
Washington IL
I was reading through the code book and noticed that in 210.52 (b) (1) the two small appliance circuits for small appliances (kitchen) can supply power to a pantry and dining room receptacles.

210.12 (B) Dwelling Units requires dining rooms (and I would assume pantries) to be protected by an AFCI device.

If you were going to supply your dining room from one or both of the two small appliance circuits; those circuits would have to be AFCI protected, Correct?

Are there any issues using GFI receptacles on a AFCI protected circuit?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
You are correct and there are no issues with AFCI and AFCI on the same circuit. I would not however, put the pantry or dining room on the counter circuits. I have never done it before the AFCI but I would not want to have issues with AFCI in a kitchen.
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
While many AFCIs have a component that behaves similar to a GFCI with around a 50 milliamp trip level, the additional arc detection component makes the AFCI a very different animal than a GFCI.

For a quick intro, read this CPSC fact sheet.

and you may want to go to Wikipedia and search on arc fault circuit interrupter.
 
Last edited:

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Back in the day, I always put the nook on a SABC in these little spec homes. But I wouldn't attempt it on an AFCI; it will work, but it could lead to many problems for the homeowner.
 