Delta B Phase to Wye Conversion

Status
Not open for further replies.

rpotts

New User
Location
La Vergne TN USA
Hello everyone!

I have a situation where I am going to need Delta B-Phase for roughly six months or so and then switch it over to a Wye configuration. I was thinking I could install some type of slug "dummy fuse" for the B Phase until I need to convert it to the Wye configuration. Is this possible to do? Is it safe?

Any solutions help!

Thanks!
Ryan Potts
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I do not understand what a "Delta B phase" means. I also don't understand what you mean by a dummy fuse, and why would you install one?
I think the OP is referring to the rule that there cannot be OCPD in a grounded conductor unless it also opens all ungrounded conductors.
If using a three phase fused disconnect, that would require replacing one fuse with a shunt.
Sent from my XT1585 using Tapatalk
 