Handhole question

Status
Not open for further replies.

steve66

Senior Member
Location
Illinois
Occupation
Engineer
See article 314

I went to look this up, and I see 314.30 and 314.28. For sizing, you need to determine if any of the conductors #4 or larger.

Splices will have to be rated for a wet location, and the manufacturers instructions will probably require a gravel bed under the handhole.
 