We need to feed a MCC with parallel feeders from an existing switchgear. The switchgear is on the 1st level. The new MCC is on a higher floor.
The plan is to run conduit from below the switchgear and route to the MCC. However, we cannot core-drill through the slab where the switchgear is on, no space in the gear for a coredrill machine.
there is one spare conduit sleeve that we can use for one feeder and its right on the section where the breaker we want to use is located. the other available sleeve is in the adjacent section.
Is it allowed by Code to cut a hole between sections to run the other set of feeder wires from a section to another section?
Is there an exception to run the other set from above the MCC?
As usual, Thanks for comments and info.