Page 1 of 2 12 LastLast
Results 1 to 10 of 19
Thread: Panel in a pantry?
  1. #1
    Join Date
    Oct 2010
    Irvine, CA
    Posts
    41
    Panel in a pantry?
    I have seen the code that says you can't install a panel in a clothes closet. What about in a pantry off the kitchen in a dwelling?
    Behind the door?
    Also, what if I build a small electrical closet within a large clothes closet?
  2. #2
    Join Date
    Mar 2009
    N of Anchrage, AK
    Posts
    172
    I can't find specific prohibition
    240.24.D,E&F tell you where you can't have OCPDs, and pantrys aren't listed. And it appears that the primary concern with clothes closets is easily combustible material in the vicinity. So, I'd think you'd be OK for putting it in a pantry, but you also need to bear in mind the working clearances in front of and to the side of the panel.
    As to building a room within a closet for the panel, I'll leave that to others to put in their 2 cents worth, but again your 30in.x36in. working clearances means it would have to be a pretty big room-within-the-room.
    Howard
    "You don't know the character of a man until there is not enough." Dr. Jack Letts, MD
  3. #3
    Join Date
    Oct 2010
    Posts
    23
    If you build a room inside of a closet you are still inside the closet. Its like going into the office of a grocery store. You are still in a grocery store.
  4. #4
    Join Date
    Aug 2008
    New England
    Posts
    1,490
    Quote Originally Posted by Howard Burger View Post
    Once the door is opened, you may have the clearance.
    "Appliances and wiring will burn out to protect fuses"
  5. #5
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,700
    Quote Originally Posted by nosparks1 View Post
    If you go into the restroom you are also still in the grocery store. If the grocery store has an electrical room it is still in the grocery store. They are dedicated spaces within the store. Where are you going with this?
  6. #6
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,967
    I think it is acceptable to build a "room" within a clothes closet, and place a panel within that room. The door to this "room" separates the overcurrent devices from the combustible materials. Working clearance might be a bit tricky, but it can be done.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  7. #7
    Join Date
    Feb 2007
    USA
    Posts
    5,629
    As long as it's not a clothes closet and there are no combustables then you should be ok
  8. #8
    Join Date
    Jun 2005
    Logan, Utah
    Posts
    8,201
    Quote Originally Posted by mike33 View Post
    As long as you have your working space clearance I would say you are OK to have a panel in a pantry.
    Behind the door?
    Behind a door is acceptable
    I agree with Charlie on this, as long as the working spaces can be met I would be OK with a closet within the clothes closet.
    Chris
  9. #9
    Join Date
    Oct 2010
    Posts
    23
    What I like about this forum is seeing many different views. If a panel was in a bathroom and someone built a cabinet with a door that met the clearance requirements around the panel, would you say the panel is no longer in the bathroom?
  10. #10
    Join Date
    Dec 2007
    California
    Posts
    591
    But the OP was not suggesting a cabinet. He was discussing an equipment closet (a seperate room) built within a clothes closet.
Posting Permissions