NEC 334 says not permitted to use NM in wet or damp locations . If i use NM in PVC or car flex nonmetalic flex outside to a A/C condenser is that allowable under the NEC?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Nope. The inside of the raceway is considered a wet location and a conductor rated for wet locations is required.
 

lakee911

Senior Member
Location
Columbus, OH
NEC 334 says not permitted to use NM in wet or damp locations . If i use NM in PVC or car flex nonmetalic flex outside to a A/C condenser is that allowable under the NEC?

It's done all the time, but no its technically not allowed. You could run NM suitable for underground burial inside of the flex. Or you could use THWN, etc.
 