Originally Posted by
Little Bill
If the tray is the EGC, then the bonding they did would suffice, yes?
It has to have some connection to the EGC of the circuits that are in the tray. The connection to building steel cannot be that connection. If the tray is physically connected to the equipment where the circuits originate and if the tray itself is suitable for use as the EGC for those circuits you are ok.
Don, Illinois
Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
(All code citations are 2017 unless otherwise noted)