Thread: Is structural steel permitted for use as a grounding conductor for cable tray?

  1. #1
    Join Date
    Jul 2011
    Location
    Port Arthur, TX, USA
    Posts
    1

    Is structural steel permitted for use as a grounding conductor for cable tray?

    At our facility there is some cable tray being installed in a pipe rack. The contractor bonded the cable tray to the supporting structural steel, but did not carry the ground down to the ground grid for the cable tray. The structural steel is grounded at the bottom. Can the structural steel be considered as an acceptable grounding conductor per the NEC?

    Thanks.

  2. #2
    Join Date
    Sep 2004
    Location
    Durham, NC
    Posts
    5,500
    Cable tray grounding Article 392.60.

    They didn't make it...You did...

    Welcome to the Forum.
    If you are even thirsty, you are two quarts low.

  3. #3
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    21,385
    Quote Originally Posted by sephorous View Post
    At our facility there is some cable tray being installed in a pipe rack. The contractor bonded the cable tray to the supporting structural steel, but did not carry the ground down to the ground grid for the cable tray. The structural steel is grounded at the bottom. Can the structural steel be considered as an acceptable grounding conductor per the NEC?

    Thanks.
    Requirements say the tray has to be connected to the equipment grounding conductor. Neither the structural steel nor the ground grid is an EGC....!!!
    I will have achieved my life's goal if I die with a smile on my face.

  4. #4
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    21,385
    Quote Originally Posted by cadpoint View Post
    Cable tray grounding Article 392.60.

    They didn't make it...You did...

    Welcome to the Forum.
    Hmmm.... cable tray grounding is 392.7 in 2008 NEC, and there are only 13 sections to Article 392.
    I will have achieved my life's goal if I die with a smile on my face.

  5. #5
    Join Date
    Dec 2010
    Location
    Tennessee NEC:2008
    Posts
    4,478
    Quote Originally Posted by Smart $ View Post
    Requirements say the tray has to be connected to the equipment grounding conductor. Neither the structural steel nor the ground grid is an EGC....!!!
    If the tray is the EGC, then the bonding they did would suffice, yes?
    If you aim at nothing, you will hit it every time!

  6. #6
    Join Date
    Sep 2004
    Location
    Durham, NC
    Posts
    5,500
    Sorry for the high numbers, I edited out a grounding article number and it seems incorrectly.

    I was bouncing in thought between many Code Articles... sorry for the confusion.
    If you are even thirsty, you are two quarts low.

  7. #7
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,435
    Quote Originally Posted by Little Bill View Post
    If the tray is the EGC, then the bonding they did would suffice, yes?
    It has to have some connection to the EGC of the circuits that are in the tray. The connection to building steel cannot be that connection. If the tray is physically connected to the equipment where the circuits originate and if the tray itself is suitable for use as the EGC for those circuits you are ok.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)

  8. #8
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    21,385
    Quote Originally Posted by don_resqcapt19 View Post
    It has to have some connection to the EGC of the circuits that are in the tray. The connection to building steel cannot be that connection. If the tray is physically connected to the equipment where the circuits originate and if the tray itself is suitable for use as the EGC for those circuits you are ok.
    It doesn't matter whether a metallic cable tray is suitable for use as an EGC. It still must be connected to the EGC of wiring it contains (or rather supports).

    392.7 Grounding.

    (A) Metallic Cable Trays.
    Metallic cable trays that support
    electrical conductors shall be grounded as required for
    conductor enclosures in accordance with 250.96 and Part
    IV of Article 250
    .

    250.86 Other Conductor Enclosures and Raceways. Except
    as permitted by 250.112(I), metal enclosures and raceways
    for other than service conductors shall be connected
    to the equipment grounding conductor.

    Exceptions omitted for brevity

    250.86 is in Part IV of Article 250.

    IMO, bonding to structural/grounding grid is okay [250.96(A)], as long as the connection to EGC requirement is met.
    I will have achieved my life's goal if I die with a smile on my face.

  9. #9
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,435
    Quote Originally Posted by Smart $ View Post
    It doesn't matter whether a metallic cable tray is suitable for use as an EGC. It still must be connected to the EGC of wiring it contains (or rather supports). ...
    That is what I said.
    It has to have some connection to the EGC of the circuits that are in the tray.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)

  10. #10
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    21,385
    Quote Originally Posted by don_resqcapt19 View Post
    That is what I said.
    I was referring to the following quoted portion of your post...

    Quote Originally Posted by don_resqcapt19 View Post
    ... and if the tray itself is suitable for use as the EGC for those circuits...
    I will have achieved my life's goal if I die with a smile on my face.