GFI protection for Elevator motor circuit

Status
Not open for further replies.

Jodonnell

Member
I have received a data sheet for an elevator. On there data sheet they are requesting a GFI circuit for the motor feeder to the Elevator. I have never hooked up an elevator on a GFI circuit. Is this a new code? I can not find anything that references a GFI circuit for an elevator.
 

DARUSA

Senior Member
Location
New York City
Some times they require a gfci line to the motor controls in or den to connect the outlet that is placed inside and outside on the top of the car elevator.
Is the motor control supplied by a transformer?if yes. is it a delta P to delta S transformer?
 

LEO2854

Esteemed Member
Location
Ma
I have received a data sheet for an elevator. On there data sheet they are requesting a GFI circuit for the motor feeder to the Elevator. I have never hooked up an elevator on a GFI circuit. Is this a new code? I can not find anything that references a GFI circuit for an elevator.

Look at 620.85 in the 2008 NEC They are looking for GFCI REC on elevator car tops:)
 