    Class 1 Div I Seals
    Are splices, taps and terminations considered arcing or sparking parts?
  2. #2
    Join Date
    Feb 2003
    Illinois
    Posts
    17,304
    No.
    Don, Illinois
    "It is the first responsibility of every citizen to question authority." B Franklin
  3. #3
    Join Date
    May 2007
    West Virginia, USA NEC: 2008
    Posts
    1,963
    It depends if you "pre-twist" or not
    I'm kidding of course, Welcome to Mike Holt's forum!
    Jack
  4. #4
    Join Date
    Jul 2004
    Texas by the Gulf, geat crab, great shrimp
    Posts
    5,104
    Quote Originally Posted by chuckbuckmo View Post
    No, but why do you have "Class 1, Div I seal" as the title of your post? What is the realtionship between the two? BTW it is Class I, Division 1. Roman numeral for Class and regular numbers for Division designation. Just sayin'
    Laszlo Z Weress
    Staff Engineer
    Business is competition, and the ultimate competition is war. All is fair in love and war.
  5. #5
    Join Date
    Apr 2004
    Laguna Hills, CA
    Posts
    3,523
    Quote Originally Posted by weressl View Post
    No, but why do you have "Class 1, Div I seal" as the title of your post? What is the realtionship between the two? ...
    I suspect it was raised by reviewing 501.15(A)(1)(2) or possibly by an influence from the IEC world where terminals are considered to be arc-making.
    "Bob"
    Robert B. Alexander, P.E.
    "I know that you believe you understand what you think the NEC says, but I am not sure you realize that what you read is not what it means.” (Corollary to Charlie’s Rule)
  6. #6
    Join Date
    Mar 2009
    Big Easy
    Posts
    256
    I would think that in Class 1 Div 1 locations abnormal circuit conditions must be considered, so terminal boxes need to be Explosion Proof to account for faulted wire conditions. Whereas in Class 1 Div 2 normal circuit operations are all that is required to be considered so terminal boxes are not required to be Explosion Proof since no faults under normal circuit operation.
  7. #7
    Join Date
    Jul 2004
    Posts
    5,104
    Quote Originally Posted by rbalex View Post
    Oh, I can speculate why it was there, but I would of rather have the OP state it than to assume what he was thinking.