    article 210.4 2008 nec

    i understand this article when installing multi wire branch circuits.
    question what if let say you install 6 circuits with 6 neutral in the same conduit entering a panel .does each circuit and neutral have to be identify as they enter a panel cant find where it says that.

  2. #2
    Join Date
    Jan 2009
    Location
    Easton, Maryland NEC: 2011
    Posts
    7,621
    I do not know of a code section requiring this identification of individual grounded conductors of circuits.

    Do not find anything in 2011 either.
    Last edited by jumper; 08-04-11 at 07:27 PM.
    "Electricity is really just organized lightning." George Carlin


    Derék

  3. #3
    Join Date
    Apr 2009
    Location
    Olathe, Kansas 338 mi SE of Wingedhorses
    Posts
    1,815
    No it's not required. But it might make it easier on the next guy if they were

    identified with sticky number wraps, especially if the next guy is YOU.
    Electricity is Color Blind
    Leave the shirt pocket rules in your pocket.

  4. #4
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    26,114
    It really is not different than 6 mc cables entering the panel. Now I believe each neutral should be identified with the appropriate ungrounded conductor.

  5. #5
    Join Date
    May 2007
    Location
    West Virginia, USA NEC: 2008
    Posts
    1,963
    Quote Originally Posted by Dennis Alwon View Post
    It really is not different than 6 mc cables entering the panel. Now I believe each neutral should be identified with the appropriate ungrounded conductor.
    following 210.4(D) each neutral of the circuit will be identified by the grouping.
    Jack

  6. #6
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    19,104
    Quote Originally Posted by Twoskinsoneman View Post
    following 210.4(D) each neutral of the circuit will be identified by the grouping.
    That does not apply to the two-wire circuits mentioned in the OP.
    Rob

    Chief Moderator

    All responses based on the 2011 NEC unless otherwise noted

  7. #7
    Join Date
    May 2007
    Location
    West Virginia, USA NEC: 2008
    Posts
    1,963
    Quote Originally Posted by grumpy11 View Post
    i understand this article when installing multi wire branch circuits.
    question what if let say you install 6 circuits with 6 neutral in the same conduit entering a panel .does each circuit and neutral have to be identify as they enter a panel cant find where it says that.
    Quote Originally Posted by infinity View Post
    That does not apply to the two-wire circuits mentioned in the OP.
    Fooled by the title of the thread saying 210.4
    Last edited by Twoskinsoneman; 08-05-11 at 10:14 AM. Reason: change thought