Thread: code inforcement inspector
  1. #1
    Join Date
    Jan 2007
    Posts
    6
    Are make shift dead fronts for a pool sub-panel allowed in the nec?
  2. #2
    Join Date
    Aug 2006
    Miami Fla.
    Posts
    6,719
    My guess would be no as per 110.3(B).
  3. #3
    Join Date
    Aug 2004
    Posts
    9,330
    Quote Originally Posted by mikekelly View Post
    Depends somewhat on what you are mean by "makeshift dead front".
    I cannot think of anything that would prohibt one from putting a door or removable panel in front of a panel board.
    Bob
  4. #4
    Join Date
    Feb 2007
    North East WA. near the big blast
    Posts
    2,783
    So are you saying that In the event that someone looses a deadfront you cannot have a metal fab make a replacement of equal thickness and material.
  5. #5
    Join Date
    Jul 2003
    MA
    Posts
    1,578
    Quote Originally Posted by Sierrasparky View Post
    I don't see any problem fabricating a dead front either.
    As long as it is a safe installation.
    Tim
    Master Electrician
    New England
    Yesterday's Technology at Tomorrow's Prices
    Answers based on 2011 NEC
  6. #6
    Join Date
    Oct 2007
    New Jersey
    Posts
    1,008
    Quote Originally Posted by tkb View Post
    Couldn't there be an issue with the panel's listing if you fabbed a replacement when you could have bought one from the manufacturer or made one for a panel that didn't have a listed dead front? I'm not talking from a practical "will it work right" perspective, but from a "who's the lawyer going to chase" perspective.
  7. #7
    Join Date
    Jul 2003
    MA
    Posts
    1,578
    Quote Originally Posted by gadfly56 View Post
    A panelboard is mounted in a cabinet, cutout box or enclosure as per 408.38.
    Cabinet, cutout box and enclosures are as per 312.
    I don't see where the cabinet for a panelbord needs to be listed execpt for nometalic cabinets as per 312.10(C).
    If I am wrong, please let me know where a listing is required.
    Tim
    Master Electrician
    New England
  8. #8
    Join Date
    Apr 2006
    Simi Valley, CA
    Posts
    6,449
    The problem usually is that, they want to make the new dead front out of sheet metal and cut it out with tin snips.
    I can build anything you want if you draw a picture of it on the back of a big enough check.
    There's no substitute for hard work....but that doesn't mean I'm going to give up trying to find one.
    John Childress
    Electrical Inspector
    IAEI / CEI / C10
    Certified Electrical Inspector
  9. #9
    Join Date
    Aug 2004
    Posts
    9,330
    Quote Originally Posted by cowboyjwc View Post
    What is the problem with that? If it is allowed, it does not matter much how it is fabricated as long as it is suitable.
    Bob
  10. #10
    Join Date
    Feb 2008
    Valley of the Sun
    Posts
    659
    I have had to do that. Sometimes you come across old equipment that you would be hard pressed to find replacement parts for and have to fabricate a replacement part. A dead front is not critical to the actual function of the panel like the breakers or buss. The one thing I would be careful of though is making sure the sheet metal was of a heavier guage similar to that of a manufacturers dead front .