I've seen addon meter lugs but...

Status
Not open for further replies.

lavacano

Chadwick Ferguson, Safe and Sound Electric
Location
Washington State
Occupation
02 master
https://photos.app.goo.gl/edS5g7eHfhIyUTYz2

I've never seen a Y-Splice inside a panel! Was this ever ok to do NEC wise (looks to be about 1980's)

If it was NEC compliant I might replace the meter with a GE PowerMark Gold, and generator interlock kit since that is what the customer is after, they can keep this ugliness if they want IMO.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Huge split bolt is exposed by poor tape job —rising near panel cover—.
That is poor workmanship, if not dangerous, relative to insulated Polaris lugs.
 

jap

Senior Member
Occupation
Electrician
My bet is that these are service entrance conductors.
Although I cant see the bonding jumper from the Neutral bar to the tub, I can see the spider sitting on what looks to be like the GEC,,, maybe not.

The Splices don't look half as bad as the buss bars around that 2p 20,,,,,

Just how far can you extend service conductors inside a residence like this anyway?

I thought it was supposed to be "at or near" the nearest point of entry.

With these being scabbed onto,,,,, how many entry's can that be ?

oh well.

JAP>
 

jap

Senior Member
Occupation
Electrician
Maybe there's a main outside and it's just not 4 wire like it should be.
If that is the case there's more corrections to be made to bring it up to date.


JAP>
 

kwired

Electron manager
Location
NE Nebraska
Though probably not the case here one could have parallel supply conductors for voltage drop reasons, and need to reduce because the lug can't take multiple conductors?
 