Results 1 to 5 of 5
Thread: 250.30(C) - Outdoor SDS Grounding
  1. #1
    Join Date
    Dec 2004
    Windsor, CO NEC: 2017
    Posts
    16,180
    Is 250.30(C) requiring us to connect to the structure served, or establish a GES at the detached structure (at the detached SDS) by, say, driving a ground rod or two?
  2. #2
    Join Date
    Dec 2010
    Tennessee NEC:2008
    Posts
    4,491
    Quote Originally Posted by George Stolz View Post
    250.30(C) is for ungrounded systems and it says to connect the GEC to the disconnecting means. To do that, you would have to run from the SDS or make one there.
    Stop it George!
    If you aim at nothing, you will hit it every time!
  3. #3
    Join Date
    Dec 2004
    Posts
    16,180
    Quote Originally Posted by Little Bill View Post
    250.30(C) is for ungrounded systems...
    Slow down - you're reading 250.32(C), not 250.30(C).
  4. #4
    Join Date
    Feb 2003
    Illinois
    Posts
    23,464
    I think this new rule is confusing. It requires that you establish a grounding electrode system at the SDS that is located outside, but it does not permit a second connection between the grounded conductor and the earth at the structure served. When I first saw this change I though it would make it just like a utility owned transformer where the grounded conductor is connected to earth both at the transformer and at the structure, I don't any wording that says you can do this with the SDS. This just requires the grounding electrode to be at the outside SDS.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)
  5. #5
    Join Date
    Dec 2010
    Tennessee NEC:2008
    Posts
    4,491
    You're right, I'm using a PDF file and when Adobe got updated it messed my search function up.
    Also, this must be in the 2011 as I don't have 250.32(C) in the 2008.
Posting Permissions
  • You may not post replies