Oversized wire?

Status
Not open for further replies.

tonype

Senior Member
Location
New Jersey
20-amp Square D breaker. Circuit wire is a #6 Al. Strands from the wire were separated and connected to the breaker, in a manner similar to double-lugging (each side of the screw). Is this proper?
 

LEO2854

Esteemed Member
Location
Ma
20-amp Square D breaker. Circuit wire is a #6 Al. Strands from the wire were separated and connected to the breaker, in a manner similar to double-lugging (each side of the screw). Is this proper?

Take a look at the circuit breaker lug and see if it rated for that size wire.

If it is then the wire should fit without the double twists
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
20-amp Square D breaker. Circuit wire is a #6 Al. Strands from the wire were separated and connected to the breaker, in a manner similar to double-lugging (each side of the screw). Is this proper?

Nope. Since you said both sides of the screw I'm assuming that you mean a QO breaker. If I remember correctly they're typically good for up to a #8 conductor. As Leo stated the listing of the CB lug would provide the correct answer. This can be a simple fix by splicing on a smaller conductor.
 

tonype

Senior Member
Location
New Jersey
Nope. Since you said both sides of the screw I'm assuming that you mean a QO breaker. If I remember correctly they're typically good for up to a #8 conductor. As Leo stated the listing of the CB lug would provide the correct answer. This can be a simple fix by splicing on a smaller conductor.

Rob: You are correct - it is a QO breaker
 

kbsparky

Senior Member
Location
Delmarva, USA
Why not simply post the pic?

SPA.jpg
 