Thread: SWEEP OF RF CABLE

  1. #1
    Join Date
    Jul 2008
    Location
    NJ
    Posts
    1,880

    SWEEP OF RF CABLE

    DOes anyone know what a "sweep" of RF cabl;e would entail/mean? Thanks.

  2. #2
    Join Date
    Jan 2009
    Location
    Easton, Maryland NEC: 2011
    Posts
    7,881
    Bending radius. Sweep elbows/ells are more gradual in the turn.
    "Electricity is really just organized lightning." George Carlin


    Derék

  3. #3
    Join Date
    Sep 2007
    Location
    MP89.5, Mason City Subdivision
    Posts
    169
    Or testing the cable with a signal generator and analyzer to make sure the cable is within spec
    Gregg

    I'm just here for the pictures!

  4. #4
    Join Date
    Jul 2008
    Location
    NJ
    Posts
    1,880
    Quote Originally Posted by grich View Post
    Or testing the cable with a signal generator and analyzer to make sure the cable is within spec
    Thanks GRICH. Can you elaborate a little more about what the test does. THanks A LOT!!

  5. #5
    Join Date
    Jun 2003
    Location
    Hawthorne, NY
    Posts
    2,414
    It tests the cable (usually coax) to see if it is within manufacturers specs. Coax can be damaged by improper handling, dents, tight bends, water ingress, high heat, age- any number of things. These things will often show up as increased attenuation at some or all frequencies depending on the defect. A sweep test applies a fixed level variable frequency signal to one end of the cable that is measured and recorded at the other. The variable frequency begins at the lowest frequency you want to measure and ramps up to the highest frequency. An X/Y axis graph is generated by the sweep receiver at the other end- frequency vs attenuation. You can then compare that to the graph provided by the manufacturer or see right off what some problems are by their "signature".

    Another useful test is with a TDR that will actually show where along the cable any problem is.


    -Hal

  6. #6
    Join Date
    Jan 2009
    Location
    Easton, Maryland NEC: 2011
    Posts
    7,881
    Sorry Horsegoer, I saw sweep and thought you were talking about installing IT cables in conduit.

    IT types are always specing oversized conduit and sweep elbows.
    "Electricity is really just organized lightning." George Carlin


    Derék

  7. #7
    Join Date
    Sep 2007
    Location
    MP89.5, Mason City Subdivision
    Posts
    169
    Quote Originally Posted by hbiss View Post
    It tests the cable (usually coax) to see if it is within manufacturers specs. Coax can be damaged by improper handling, dents, tight bends, water ingress, high heat, age- any number of things. These things will often show up as increased attenuation at some or all frequencies depending on the defect. A sweep test applies a fixed level variable frequency signal to one end of the cable that is measured and recorded at the other. The variable frequency begins at the lowest frequency you want to measure and ramps up to the highest frequency. An X/Y axis graph is generated by the sweep receiver at the other end- frequency vs attenuation. You can then compare that to the graph provided by the manufacturer or see right off what some problems are by their "signature".

    Another useful test is with a TDR that will actually show where along the cable any problem is.


    -Hal
    Thanks, Hal for answering while I was out inspecting an AM transmitter site...you 'splained it better than I could, anyway.

    Our Fluke DTX1800 can sweep coax up to 900MHz as part of its testing, although we didn't buy the coax interface kit...we just use it to certify our CAT6 runs.
    Gregg

    I'm just here for the pictures!

  8. #8
    Join Date
    Sep 2007
    Location
    MP89.5, Mason City Subdivision
    Posts
    169
    Quote Originally Posted by jumper View Post
    ...IT types are always specing oversized conduit and sweep elbows.
    You'd be surprised how fast those conduits fill up sometimes. Gotta have the sweeps to respect minimum bend radius specs, and to make it easier on this old man pulling cable.
    Gregg

    I'm just here for the pictures!

  9. #9
    Join Date
    Jan 2009
    Location
    Easton, Maryland NEC: 2011
    Posts
    7,881
    Quote Originally Posted by grich View Post
    You'd be surprised how fast those conduits fill up sometimes. Gotta have the sweeps to respect minimum bend radius specs, and to make it easier on this old man pulling cable.
    I got no problem with that, except many times I have ran a 2" conduit and sweeps and it turns out to be 2-3 Cat 5 cables. I get paid by the hour, so: not my problem.
    "Electricity is really just organized lightning." George Carlin


    Derék

  10. #10
    Join Date
    Feb 2009
    Location
    Durango, CO
    Posts
    3,555
    What we need is more IT guy engineering and less value engineering. That would be a way to fuel the economy.