    can a 3 pole 4 wire receptacle (15-50r) be used on a 70 amp circuit using a 3 pole 70 amp breaker and #4THHN?
  2. #2
    Join Date
    Feb 2003
    Connecticut
    Posts
    2,937
    Quote Originally Posted by jbalsamo View Post
    No, this would be a violation of 210.21(B)(1) for a single receptacle circuit or 210.21(B)(3) for a multiple receptacle circuit (unless you meet any of the exceptions therein.)
  3. #3
    Join Date
    Sep 2011
    Ft Lauderdale, FL
    Posts
    4
    would an exception being a single receptacle for a welding outlet and dedicated use?
  4. #4
    Join Date
    Feb 2003
    Connecticut
    Posts
    2,937
    A dedicated single receptacle for an Arc-welder is one of the exceptions.
  5. #5
    Join Date
    Sep 2011
    Ft Lauderdale, FL
    Posts
    4
    Thank you!