    50 plug using a 70 amp breaker and 70 amp rated wire

    can a 3 pole 4 wire receptacle (15-50r) be used on a 70 amp circuit using a 3 pole 70 amp breaker and #4THHN?

  2. #2
    Join Date
    Feb 2003
    Location
    Connecticut
    Posts
    2,254
    Quote Originally Posted by jbalsamo View Post
    can a 3 pole 4 wire receptacle (15-50r) be used on a 70 amp circuit using a 3 pole 70 amp breaker and #4THHN?
    No, this would be a violation of 210.21(B)(1) for a single receptacle circuit or 210.21(B)(3) for a multiple receptacle circuit (unless you meet any of the exceptions therein.)

  3. #3
    Join Date
    Sep 2011
    Location
    Ft Lauderdale, FL
    Posts
    4
    would an exception being a single receptacle for a welding outlet and dedicated use?

  4. #4
    Join Date
    Feb 2003
    Location
    Connecticut
    Posts
    2,254
    Quote Originally Posted by jbalsamo View Post
    would an exception being a single receptacle for a welding outlet and dedicated use?
    A dedicated single receptacle for an Arc-welder is one of the exceptions.

  5. #5
    Join Date
    Sep 2011
    Location
    Ft Lauderdale, FL
    Posts
    4
    Thank you!