Page 1 of 3 123 LastLast
Results 1 to 10 of 23
Thread: NM cable wet/damp locations
  1. #1
    Join Date
    Nov 2007
    Posts
    858
    How many here are still running indoor NM cable in a Carflex or sealtite sleeve to a piece of outdoor equipment? I have been doing it for years and never had an issue with it until now. Seems as though now we have to either transition to THHN or UF type cable for this application. Inspector is considering it a damp location and will not allow indoor NM to be used. Have I been violating the code all along, or has it just not been enforced. Thanks.
  2. #2
    Join Date
    Feb 2003
    Minnesota
    Posts
    6,689
    Quote Originally Posted by nizak View Post
    I remember my master taught me to use NM when I apprenticed, but when I started working on my own, the inspectors (in a more rigorously enforced area) caused me to understand the limitation of NM to dry locations.
    Another Al in Minnesota
  3. #3
    Join Date
    Jan 2007
    Massachusetts
    Posts
    2,476
    Both.
  4. #4
    Join Date
    Dec 2010
    Tennessee NEC:2008
    Posts
    4,418
    The code changed to say that the inside of raceways above grade is considered a damp location.
    If you aim at nothing, you will hit it every time!
  5. #5
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by Little Bill View Post
    I disagree with that, in my opinion the code has considered that a wet location for many code cycles but recently the code was changed to make it perfectly clear.
  6. #6
    Join Date
    Dec 2010
    Tennessee NEC:2008
    Posts
    4,418
    Quote Originally Posted by iwire View Post
    I didn't say when it changed.
  7. #7
    Join Date
    Dec 2006
    Eastern Oregon
    Posts
    3,452
    I don't run it in flex whips to equipment outside(use THHN), but I have sleeved it in short stubs from an outdoor panel into the attic/crawlspace above or below the panel. I'm not going to run it in conduit all the way down the side of a house or anything, even though that's not any less of a violation than what I have been doing.
    I hate to say it, but we're in such dry country over here, I'll keep doing it this way until I get called on it. I hate UF, and really don't care to use it until I absolutely have too.
  8. #8
    Join Date
    May 2008
    Maryland
    Posts
    112
    Do you transition from NM to THWN or UF when connecting to an exterior wall mount coach light/wall pack or generator power inlet box on a residential building?....or do you just run NM straight to the exterior fixture/inlet box?
    Bernard
  9. #9
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    14,193
    Quote Originally Posted by Bernard1599 View Post
    Bernard
    Straight in.
    "Electricity is really just organized lightning." George Carlin
    Derek
  10. #10
    Join Date
    May 2008
    Maryland
    Posts
    112
    Quote Originally Posted by jumper View Post
    Straight in.
    Have you ever been called out for it? 2008 - 334.12 (B) (4)?
    Bernard