    Existing 800a 208Y UG service. Utility CT cabinet and 800a MCB N3R distribution panel SUSE located on outside wall. Installation of a 100kw gen set and 800a auto xfr sw to back up service is required. AHJ (local building inspector) will allow a non-suse xfr sw fed from the CT cabinet and the load side to re-feed the 800a SUSE panel due to the location, right next to the panel.
    Question is, doesn't the xfr switch need to be SUSE listed?
  2. #2
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Yes it does.
  3. #3
    Join Date
    Sep 2011
    WI
    Posts
    80
    Thanks Bob. New to the forum, appreciate the reply. The proper application did seem obvious.
  4. #4
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,321
    Probably so obvious that I am overlooking it... what is SUSE?
  5. #5
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    14,191
    Quote Originally Posted by kwired View Post
    SEU or USE is my guess.
    "Electricity is really just organized lightning." George Carlin
    Derek
  6. #6
    Join Date
    Sep 2011
    WI
    Posts
    80
    Suitable for use as service equipment
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,321
    Quote Originally Posted by GearMan View Post
    Quote Originally Posted by jumper View Post
    I don't think that is it, he asked if the transfer needs to be SUSE listed. I'm thinking something along the lines of service rated transfer switch but am lost as to just exactly what SUSE would be an acronym for.
  8. #8
    Join Date
    Jan 2009
    Posts
    14,191
    See post #6. The term escaped me also. The code never says "service rated".
    230.66 Marking. Service equipment rated at 600 volts or
    less shall be marked to identify it as being suitable for use
    as service equipment. Individual meter socket enclosures
    shall not be considered service equipment.
    225.36 Suitable for Service Equipment. The disconnecting
    means specified in 225.31 shall be suitable for use as
    service equipment.
    Derek
  9. #9
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,321
    Ok it finally penetrated my skull. I even read post 6 and it did not sink in the first time.
  10. #10
    Join Date
    Feb 2003
    Wisconsin
    Posts
    9,855
    Actually there are several different service entrance ratings available, SUSE is just the more commonly mentioned one.
    Suitable for Use as Service Entrance (SUSE) equipment comes with a neutral to ground bonding jumper, for field installation/removal. Most panels and disconnect switches are built like this.
    Suitable for use only as service equipment comes with a neutral to ground jumper that is factory installed and not removable. All-in-one (meter+distribution), panels are built like this.
    Actually there are additional requirements that are apply to service equipment.