NEC 610.14(A) Ampacity for Crane Feeders

Status
Not open for further replies.

jlee405

Member
Location
Seattle
How would i figure out the equivalent short-time aluminum ampacities for crane feeders. Table 610.14(A) only lists ampacities for copper. Or does this imply that I cannot use aluminum for feeders to cranes?
 

Mechfly

New User
Location
Manteca Ca USA
Ampacity for Aluminum Feeders

Ampacity for Aluminum Feeders

Article 100 explains...

110.5 Conductors. Conductors normally used to carry current shall be of copper unless otherwise provided in this Code. Where the conductor material is not specified, the material and the sizes given in this Code shall apply to copper conductors. Where other materials are used, the size shall be changed accordingly.
 