210.12 Arc Fault

Status
Not open for further replies.

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
does the Bar under counter refridgerator require AFCI protection? although in the family but the fridge is a dedicated sace
Yup. Remember, 210.12 is about outlets, which is defined in Article 100 Definitions. An outlet can be a duplex receptacle, single receptacle, luminaire, smoke detector, hardwired appliance (like a dishwasher or a baseboard heater), etc. If the outlet is 120 Volt 15 or 20 Amp in a designated area or room listed in 210.12, then the AFCI gets installed.
 
Status
Not open for further replies.