    220.54 & 220.55: Single Phase Panels & Three Phase Service

    Article 220.54 in the 2008 NEC states the following:

    "Where two or more single-phase dryers are supplied by a 3-phase, 4-wire feeder or service, the total load shall be calculated on the basis of twice the maximum number connected between any two phases."

    Article 220.55 has a very similar sentence:

    "Where two or more single-phase ranges are supplied by a 3-phase, 4-wire feeder or service, the total load shall be calculated on the basis of twice the maximum number connected between any two phases."

    My question is: What are you supposed to do if you have single-phase dryers and single-phase ranges on single-phase panels fed by a three-phase service? None of the examples I have found in the NEC cover this situation. Such a situation could occur for a multifamly dwelling.

    Do you calculate as though the dryers and ranges were on three-phase panels (even though they are not) and take twice the maximum number that would be connected between any two phases if they were on a three-phase panel? (Case#1.)

    Or do you take twice the maximum number that would be connected between any two phases on the single-phase panel that they are each on? (Case #2.)

    Or does the requirement above not apply because the dryers and ranges are not directly supplied by a 3-phase feeder or service? (Case #3.)

    For example, say you had a multifamily dwelling fed by a three-phase service. There are 10 dwellings and each is served by a single-phase panel. Each dwelling has a single-phase dryer and single-phase range.

    Using the cases defined above, you would come up with the following number of dryers and ranges as the basis of your calculation:

    Case #1: 4 x 2 = 8
    Case #2: 10 x 2 = 20
    Case #3: 10

    As you can see, how the code is interpreted makes a big difference.

    I appreciate any insight into this topic. Thanks.

  2. #2
    Join Date
    Feb 2003
    Location
    Connecticut
    Posts
    2,149
    See the Example D5(a) in Annex D. It is a situation like you describe. Essentially, it would be based on Case #1 (4x2=8) but it is a little more complicated that that.

  3. #3
    Join Date
    Oct 2011
    Location
    Portland, Oregon, U.S.
    Posts
    2
    Thanks David! I didn't notice that example D5(a) was using single-phase panels to feed the individual dwelling units. I didn't recognize that the phrases "Service to each dwelling unit would be two phase legs and neutral" and "120/208-V, 3-wire system" implied that the dwelling units were using single-phase panels. I appreciate the help.