NEC 230.70 (A) Service Equipment disconnecting means

Status
Not open for further replies.

codequestion

Banned
Location
MD, USA
I have one utility electric condcutors to trough from which four feeders go to four meters. Two of the four meyers are for futire use.

The other two of the four meters go to two panelboards inside building. The panelboards have main breaker. There is no disconnecting means outside two meters.

Would this be complaint with nec 230.70 (A)?

Sent from my SM-G935U using Tapatalk
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Depends on how the conductors got to the panelboards.

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Going from meter outside of building entering at wall room outside panelborad into the panelboard.

Sent from my SM-G935U using Tapatalk
Sounds like it complies with 230.70(A)(1).