    Conduit Bodies - Class II Div.2 Group G

    Which Form Type of conduit body is approved for Class II, Div.2, Group G locations? I have searched the manufacturer's specs and they do not call out a specific listing.

    We have in our stocked parts cage the Mark 9 type and we are considering the use of Form 7 for an upcoming Class II, Div.2, Group G installation. We need to get something on order if we cannot use the Mark 9.

    What is approved and suggested for "best industry practice"?

    thanks for your answers...

  2. #2
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    4,023
    This is one of the cases that Section 500.8(A)(3) was written for.

    The ruling text is in Section 502.10(B)(4), “Boxes and Fittings. All boxes and fittings shall be dusttight.” While dusttight is a defined term (in two places as a matter of fact - an NFPA Manual of Style no-no), it isn’t defined too rigorously. Conduit body is also defined, but it doesn’t exempt a conduit body from being a “box.”

    You won’t find any conduit body listed specifically for Class II, Division 2 or as dusttight –because they don’t need to be. Conduit bodies listed for Class II are dust-ignitionproof which is gross overkill for dusttight.

    Personally, I wouldn’t hesitate to use either Form 7 or Mark 9 in Class II, Division 2. If I were REAL concerned, I might tuck in a gasket, but I probably wouldn’t. And before anyone cautions me about using gaskets in Classified locations, don’t bother since there is no attempt to maintain either an explosionproof (which doesn’t apply) or dust-ignitionproof rating in Class II, Division 2. Besides, that general prohibition has been gone a long time as long as the gasket/O-ring doesn’t interfere with the intended flame-path.
    "Bob"
    Robert B. Alexander, P.E.
    "I know that you believe you understand what you think the NEC says, but I am not sure you realize that what you read is not what it means." (Corollary to Charlie's Rule)