I do not have the 2011 on hand, but NEC 2002 702.6 requires transfer equipment, not sure if 2011 is the same article.
In a discussion with a co-worker I say the grounded conductor does not need to be switched, only the ungrounded. He insists that in years past ungrounded and grounded needed to be switched.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I am not aware of any older code requirement that required the grounded conductor of a generator to be switch with the transfer switch. As far as I am aware this has always been a design issue not a code issue.