If you take a resistance reading with a dmm and it is set on auto, and the reading shows "M" for Mega (example, 18.42 M Ohm's), I'm assuming that would be equivalent to 18,420,00 Ohm's?

I had a brain fart today while troubleshooting some tile floor heat, related to their rated resistance and have been second guessing myself all afternoon!

The heating element is rated for 16 Ohm's. It's not putting out heat. No current draw at t-stat.
Not sure if heating element was compromised during tile install. Was ohm'ing out the leads to element and definitely didn't get 16 Ohm's. Tried a couple of meters with similar results.

After figuring this out, then need to interpret those results...

Moderators, if you feel this belongs in different section feel free to move it...
Thanks!
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Yes, M for Mega means that you multiply the reading by one million, 1,000,000.
While K for Kilo means that you multiply the reading by one thousand, 1,000.

A reading of 18Megohms is for all practical purposes an open circuit. (Although a higher voltage than is used by your DMM might break down a tiny insulating gap somewhere.)

Note also that the presence of any residual voltage on the disconnected wires, even as little as phantom voltage in some cases, can interfere with the reading process on some DMMs.
 

sw_ross

Senior Member
Location
NoDak
Yeah, I was just playing with the calculator, nameplate-> 16 Ohm's at 120v is 7.5 amps and 900 watts. What I saw-> 18.42M Ohm's is basically 0 amps and watts!

I'm guessing the heating element got damaged...
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Yeah, I was just playing with the calculator, nameplate-> 16 Ohm's at 120v is 7.5 amps and 900 watts. What I saw-> 18.42M Ohm's is basically 0 amps and watts!

I'm guessing the heating element got damaged...


Once they develop a hot spot for any reason eventually the heater wire will burn through at that point.
Even nichrome wire increases in resistance when it gets really hot.
 

MTW

Senior Member
Location
SE Michigan
It would be wise to test the cable heating element and cold extension leads, before the floor installers show up. That way you would know who owns the problem.

MTW
 

kwired

Electron manager
Location
NE Nebraska
A reading of 18 MΩ is likely to be the resistance of your fingers.
Yes, if OP was contacting probes while testing he could have been reading through himself, always make sure you are never touching more then one probe when testing results is in meg-ohm range.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
I thought this was going to be the one about Mega Ohm and Milli Amp going out into an electric field and fluxing. :D
 