    testing wire integrity

    How can you test the wire integrity before connecting to main line power, I am putting 120/208 three phase and I would like to test before connecting main power. I learn how to use the megger but I don't have one, and I would like to use my volt meter and put it in Ohms or Continuity and go from there but I am not exactly one hundred percent sure any tips?

  2. #2
    Join Date
    Jun 2008
    Location
    Campbell CA
    Posts
    226
    Quote Originally Posted by ismaelbucio View Post
    How can you test the wire integrity before connecting to main line power, I am putting 120/208 three phase and I would like to test before connecting main power. I learn how to use the megger but I don't have one, and I would like to use my volt meter and put it in Ohms or Continuity and go from there but I am not exactly one hundred percent sure any tips?
    The only test you can do at this time is insulation resistance test, which that is accomplished by applying voltage for a certain amount of time to the wire. Megger does generate voltages needed to do this test, but a normal volt meter is not a right tool for that.

  3. #3
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    19,244
    A regular meter will not do an insulation test, it is still a good idea to at least do a continuity check in case there is a short circuit or ground fault before turning power on. Any continuity where it does not belong is a bad thing, and you especially would not want to be plugging in a POCO meter while live if that is the case. (Even though you are not supposed to plug meters in while live)

  4. #4
    Join Date
    Jul 2004
    Location
    Ca and Wa
    Posts
    1,486

    OJT

    Quote Originally Posted by ismaelbucio View Post
    How can you test the wire integrity before connecting to main line power, I am putting 120/208 three phase and I would like to test before connecting main power. I learn how to use the megger but I don't have one, and I would like to use my volt meter and put it in Ohms or Continuity and go from there but I am not exactly one hundred percent sure any tips?
    Depending on the extent of testing a BC or complete system, a hi-pot test would best check the conductor insulation strength for any dielectric weakness or damage that may exist against a complete grounded/grounding system. i noticed your profile of possibly being in an USAF affiliate, you may have an opportunity to get into a training program that may have available hi-pot testing of both aircraft and Ground support equipment cabling validation. (Note that hi-pot levels can have breakdown results from improper test settings.)
    rbj, Seattle...Safety is a Professional Courtesy.

  5. #5
    Join Date
    Mar 2008
    Location
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    5,880
    Quote Originally Posted by gndrod View Post
    Depending on the extent of testing a BC or complete system, a hi-pot test would best check the conductor insulation strength for any dielectric weakness or damage that may exist against a complete grounded/grounding system. i noticed your profile of possibly being in an USAF affiliate, you may have an opportunity to get into a training program that may have available hi-pot testing of both aircraft and Ground support equipment cabling validation. (Note that hi-pot levels can have breakdown results from improper test settings.)
    Some cables will have their warranty voided if a hi-pot test is done on them. Technically, it is a form of destructive testing.

    I would check with the mfg. of the cable before doing any hi-pot testing.
    Cheers and Stay Safe,

    Marky the Sparky