I concur with sgunsel with regard to checking the correct classification(s). Assuming the locations are classified correctly:

Originally Posted by
Andy Nagel
We are currenty doing a remodel of an existing spray room that is classified as a class 1 division 2 hazardous location. The original build was done in the 70's. I had some questions regarding the current locations of the conduit seal off's. For the lighting there are seal off's on each side of a junction box [OK] that splits off to feed the (3) seperate switch locations. Being that the switches are less then three feet from the j box there is only the one seal off in each run. [OK if each seal is within 18” of both J-box and switch] Leaving each switch there is a seal off on each conduit [OK] that goes up to it's respective row of class 1 div 2 lights in the spray room. There is not a seal off on the conduit as it enters the explosion proof light [OK], nor are there any on the conduits between the next 6 lights in each [OK]. At these lights the conduit enters a box that is part of the fixture that has the 3/4" hubs along with another threaded access hole on the side that appears that it is there for makeup purposes. Are seal off's not required at boxes used for makeup? [Not in Division 2] In some of these runs between lights that don't have seal off's there are unions. [Still OK] Does this change whether or not a seal off is required between makeup boxes? [NO]
We will also be adding some new fire alarm devices in this room. Currently there is a heat detector in the room that doesn't have a seal off at the device, but has one in the run after it exists the classified location. Is this a proper install? [Possibly, would need to know the enclosure ratings of the detector] Does fire alarm need seal offs between devices inside a hazardous location? [Possibly, would need to know the enclosure ratings and internals of the devices]
Lastly, there are a couple added "hazmat" rooms (sounds like it may be for paint storage) that are all sharing common walls. Are seal offs required when going from one classified location into another, [I prefer it when the locations are not classified by the exact same source(s); however, it is technically not an NEC requirement as long as the locations are the exact same Class, Division, Group and “T”-rating] or are they only required when exiting/entering a hazardous location?
"Bob"
Robert B. Alexander, P.E.
"I know that you believe you understand what you think the NEC says, but I am not sure you realize that what you read is not what it means.” (Corollary to Charlie’s Rule)