Even though the cable is bonded on the supply end what happens if there is a ground fault to the connector at the load end? If the cable is fairly long the jacket my not allow enough current to open the overcurrent device before generating enough heat to start a fire. That is the reason that other flexible wring methods are not listed as the EGC in lengths over 6'. Without grounding bushing installed on the connector I would not accept the installation either.