    open delta

    Is open delta trasformer considered one phase or two
    How two phasa looks like

  2. #2
    Join Date
    Feb 2003
    Location
    Wisconsin
    Posts
    8,718
    An open delta is a three phase system.
    Just because you can, doesn't mean you should.

  3. #3
    Join Date
    Jul 2009
    Location
    Ware Shoals, South Carolina
    Posts
    1,069
    I know it does not look like it could be 3-Phase with only two single phase transformers, but it is.
    See this website:
    http://www.3phasepower.org/3phasetransformers.htm
    Advise is a dangerous gift, even from the wise to the wise.

  4. #4
    Join Date
    Jan 2009
    Location
    Easton, Maryland NEC: 2011
    Posts
    7,465
    Cheap, economical, and efficient 3 phase service. Less power, 57% I think.
    "Electricity is really just organized lightning." George Carlin


    Derék

  5. #5
    Join Date
    Feb 2003
    Location
    Wisconsin
    Posts
    8,718
    Quote Originally Posted by jumper View Post
    Less power, 57% I think.
    Old wives tale, kind of.

    If you have a bank of three transformers and then remove one of them, your are correct the result will be 57.7% of the designed amount you started with.

    However, a bank designed using only 2 transformers can deliver 100% of its design.
    Just because you can, doesn't mean you should.

  6. #6
    Join Date
    Feb 2003
    Location
    United States
    Posts
    386

    Open-Delta Transformer Connections

    As a transformer bank the use of open-delta is relatively inefficient where most of the loads are three-phase since the bank has only 86.6% of the rating of the two units making up the three-phase bank. It also has only 57.7% of the three-phase rating of the closed delta bank of three units. When the open-delta bank is used because the three-phase loads are small, you find transformers of different sizes being used. A larger transformer for the single-phase load and a smaller transformer for the lesser, three-phase loads.

  7. #7
    Join Date
    Dec 2010
    Location
    -
    Posts
    1,505
    While we are on this subject, Where (cos 30º) =.866, Where does the 30º shift come from? Why is it there?

  8. #8
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    18,105
    Quote Originally Posted by jim dungar View Post
    Old wives tale, kind of.

    If you have a bank of three transformers and then remove one of them, your are correct the result will be 57.7% of the designed amount you started with.

    However, a bank designed using only 2 transformers can deliver 100% of its design.
    Quote Originally Posted by grant View Post
    As a transformer bank the use of open-delta is relatively inefficient where most of the loads are three-phase since the bank has only 86.6% of the rating of the two units making up the three-phase bank. It also has only 57.7% of the three-phase rating of the closed delta bank of three units. When the open-delta bank is used because the three-phase loads are small, you find transformers of different sizes being used. A larger transformer for the single-phase load and a smaller transformer for the lesser, three-phase loads.
    This is true with three transformers of the same size and then you remove one. There are cases where there is larger transformer for the two 120 volt to ground phases because there is more load on those phases - then 57% changes even more, or there are even three transformer banks that still have a larger unit for 120 volt phases but two smaller units for the others - again because the 120 volt load is expected to be larger than the loads connected to the 208 volt phase.

  9. #9
    Join Date
    Dec 2010
    Location
    -
    Posts
    1,505
    Quote Originally Posted by kwired View Post
    This is true with three transformers of the same size and then you remove one. There are cases where there is larger transformer for the two 120 volt to ground phases because there is more load on those phases - then 57% changes even more, or there are even three transformer banks that still have a larger unit for 120 volt phases but two smaller units for the others - again because the 120 volt load is expected to be larger than the loads connected to the 208 volt phase.
    Could you explain how the 57.7% changes based on the size of XF's? If I need more than a 25 kVa for the power pot, it needs to be closed IMO.

  10. #10
    Join Date
    Jan 2012
    Location
    Philly Pa burbs
    Posts
    636
    Quote Originally Posted by Hv&Lv View Post
    While we are on this subject, Where (cos 30º) =.866, Where does the 30º shift come from? Why is it there?
    Are you talking about the delta/wye 30º phase shift?