Size #18 AWG Switch Leg???

Status
Not open for further replies.

bvano1983

Member
Location
El Paso, TX
I'm working in an elementary school changing out ballasts and yesterday noticed that one of my 2 switch legs going into a 4 lamp fluorescent fixture is a size #18 and the other is a #12. Table 310.5 shows that the minimum size is a #14. Why and when is this #18 permitted to be used?

Fixture: 4 Lamp Fluorescent w/ 2 Ballasts
Conduit: 1/2" EMT
Conductors entering fixture: #12 Red, #18 Black, #12 Green, #12 White.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
#18 AWG conductors are not permitted as conductors for general permise wiring.

#18 can be used as a fixture wire in accordance with 240.5 and can be tapped from a 20 amp circuit for lengths up to 50 feet.

Chris
 

LEO2854

Esteemed Member
Location
Ma
I'm working in an elementary school changing out ballasts and yesterday noticed that one of my 2 switch legs going into a 4 lamp fluorescent fixture is a size #18 and the other is a #12. Table 310.5 shows that the minimum size is a #14. Why and when is this #18 permitted to be used?

Fixture: 4 Lamp Fluorescent w/ 2 Ballasts
Conduit: 1/2" EMT
Conductors entering fixture: #12 Red, #18 Black, #12 Green, #12 White.

I don't think that was ever allowed.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
A switch leg must be the same size as the circuit conductors. Unless the cir. is 15 amps then a 14 awg is not allowed.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Sounds like someone misused a pre-made fixture-whip wire or a ballast wire. One normally does not carry #18 building wire.
 