    Quote Originally Posted by ritelec View Post
    Take back "guess unless designed", I see no exemptions.

    ??? I see nothing mentioning recpts have to be hospital grade.???

    Is it in there or is that an architect thing? Will look again.
    Look at 517.18(B),517.19(B)(2), 517.61(C)(2).

    OP did not say what he had other than patient care facility, he may not need them depending on exactly what type of care is provided.

    Not sure where you were going with isolated ground - for most part not acceptable in patient care areas.

  3. #13
    Join Date
    Sep 2004
    Location
    Durham, NC
    Posts
    5,285
    Check your State requirements, the exact type and limit of a partical type of constuction methods might well add not detact from your thoughts!
    If your even thirsty, your two quarts low.

  4. #14
    Join Date
    Jun 2009
    Location
    NW Indiana
    Posts
    269
    The gents that have answered know best, but I'd question why you don't have the spec book(s) Div 16, anyway. Find out for sure. No reason to bid the wrong material. That would automatically exclude you in my book.

  5. #15
    Join Date
    Feb 2006
    Location
    Jersey
    Posts
    1,404
    Quote Originally Posted by kwired View Post
    Look at 517.18(B),517.19(B)(2), 517.61(C)(2).
    Thank you for the heads up kwired

  6. #16
    Join Date
    Apr 2007
    Location
    Huntington Beach, CA (21 Hrs. 32 Min. from Winged Horses)
    Posts
    3,618
    Quote Originally Posted by mike7330 View Post
    "This is a step up from the custom homes and strip stores I'm comforble bidding on, would hate to start off in the hole"
    READ THE SPECS!!! wiring a patient care facility is not the same as custom homes and strip stores, I'm sure you can do the job. but make sure you bid with the correct wiring and /or piping.
    and depending on exactly what type of facility and where it's located, you might find yourself
    with your first lesson in OSHPD.... for what it's worth, you really need to know if your job is
    under jurisdiction of OSHPD... it will drastically affect your profit on the job if you make
    assumptions where they are doing the inspection.

    http://www.oshpd.ca.gov/

    my last job with an oshpd resident inspector was sorta like darth vader with a book of specs,
    but not as much fun.
    Last edited by Fulthrotl; 02-07-12 at 03:32 AM.
    “Give a person a fish and you feed them for a day;
    teach that person to use the Internet and they won't bother you for weeks.”

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •