I have a gas fired pool heater and an ionization unit to hook up.

I know the pump motor requires GFCI protection and from what I can see the other two items do not.

Both items mentioned come from the manufacturer with a cord.

Neither have a male cord end, just conductors.

Am I correct ?

Thanks
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The gas fired pool heater needs gfci in the 2017 nec if it is powered above the low voltage limit


680.28 Gas-Fired Water Heater. Circuits serving gas-fired
swimming pool and spa water heaters operating at voltages
above the low-voltage contact limit shall be provided with
ground-fault circuit-interrupter protection for personnel.
 

blkmagik21

Senior Member
Location
Kennewick
In the 2017 code hydraulic pumps for auto covers have to be gfci protected too. I’m not a big fan of the many gfci additions to the new 2017 code.