This may be a simple question, but I'm having trouble finding an authoritative answer. Is there a UL or NEC document that requires whether the larger or smaller voltage comes first?
For example, should a portable power distribution panel be marked 208/120V or 120/208V? Out of habit I've typically used the larger voltage first because that would usually drive component selection and spacing requirements. But I have not been able to find a written specification that requires one or the other.
Thanks,
Steve Takata
It depends on if it is single phase or three phase.
One document to look at is the 'Red Book' IEEE STD 141 which is based on ANSI C84.1.
The simple methodology is:
For single phase systems use LV/HV, such as 120/240
For three phase systems use HV/LV, including the symbol Y when applicable such as 240/120 and 208Y/120.
Industry standards are really just suggestions, so it is likely you will find exceptions to this methodology.
Just because you can, doesn't mean you should.