Can we parallel 1 conductor of a feeder and not the others?

Example 1: 400 amp 3-phase feeder with 2 x 600mcm THWN copper and 1-set of parallel THWN 4/0 copper in same raceway for ungrounded phases with full size grounded conductor and correctly sized EGC per 250.122?

Example 2: 400 amp 3-phase feeder with 3 x 600mcm copper THWN ungrounded phase conductors and 1-200% neutral in parallel with correctly sized EGC per 250.122?

310.10(H) does not seem to prohibit paralleling 1 conductor?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You only need to ensure that each phase has the same size parallel conductors. For example: A phase could be parallel 600's, phase B could be parallel #3/0's and phase C parallel 500's.
 

nickelec

Senior Member
Location
US
Being that the ungrounded conductors for each phase need to be ran in the same conduit it would be kind of odd to see 1 600 MCM + 2 4/0 in 1pipe and the same in the other two
You can't run phase A in one conduit phase B in the next and face C in the next

Sent from my SM-G950U using Tapatalk
 

nickelec

Senior Member
Location
US
It may not be a violation but would definitely make you scratch your head if you seen it on site

Sent from my SM-G950U using Tapatalk
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It may not be a violation but would definitely make you scratch your head if you seen it on site

Sent from my SM-G950U using Tapatalk

I don't think one would scratch too long to figure it out. They may wonder why but one will figure it out.
 