fisherelectric
Senior Member
- Location
- Northern Va
Customer has a 40 KW generator that's been wired for 120/240 volt operation with a 180 amp breaker. His house has 2 200 amp service disconnects in the garage with 4/0 SER feeders running to load centers in the basement. He wants to install 2 manual 200 amp transfer switches between the disconnects and the load centers. He wants to run 4/0 SER from the generator to a trough beside the transfer switches and then run 4/0 into each transfer switch. Is that compliant?
He has gas heat and cooking and water heater. Five small AC units the largest of which has MCA 22 amps.
He has gas heat and cooking and water heater. Five small AC units the largest of which has MCA 22 amps.
Last edited: