Good afternoon, I have a situation I would like to know if some of you is familiar with.An HVAC unit can be separate into two point power connection.
Circuit 1(CTRL’s, Blower, PE, ERV)
FLA: 18 amps
MCA: 19.9 amps
MOP: 25 amp
Circuit 2(Comp’s, Cond’s, G. Heater)
FLA: 47.5 amps
MCA: 52.5 amps
MOP: 70 amp
Circuit 1 would be connected to an emergency panel, while While Circuits 2 would be connected to a Non-emergency panel.
Does anybody knows if that is code violation?
Thank you in advances!