Table 450.3(B) indicates that there are two (2) methods for Protection: 1) Primary only protection and 2)Primary and Secondary Protection.

When are we required to provide secondary protection?

Do we need secondary protection if we have a current of 9 amperes or more and the primary protection circuit breaker is sized within 125% of the transformer-rated current?
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Table 450.3(B) indicates that there are two (2) methods for Protection: 1) Primary only protection and 2)Primary and Secondary Protection.

When are we required to provide secondary protection?

Do we need secondary protection if we have a current of 9 amperes or more and the primary protection circuit breaker is sized within 125% of the transformer-rated current?

Article 450 is only part of the story for transformer OC protection requirements. As Dennis mentioned see 240.21(C), specifcally 240.21(C)(1). In most cases you will always need secondary protection as most installations are not a 2 wire secondary.
There is a valid reason for this. Care to think of why?
 